    MV40 alarm 12

    I have an MV40 with Fanuc controls that is has alarm 12 which has to do with cables,motor or amp short.I've checked the cables and motor with a megger with good readings.Sent in the amp for repair and Fanuc had to do "minor" repairs but tested ok---until I got it back in the machine.Any thoughts??

  2. #2
    Join Date
    Jan 2006
    Posts
    59
    Does it have the alarm 12 at power up?

    If so remove the output wires to the motor and power up again and see if the alarm is still there.

    Another quick test would be to run the spindle as slow as you can and check to see if it is smooth or not.

    It is still possible the drive could be defective.

    RRL

  3. #3
    Join Date
    Aug 2008
    Posts
    153
    Alarm 12 on a Fanuc AC spindle drive means that excess current flowed in the drive. If the board is good, there is most certainly a shorted power transistor module. Fanuc's spindle maintenance manual has a few pages on how to test the modules. Be careful when changing the modules - the wires aren't marked.

    Warren
    www.uptimecorp.com

Similar Threads

  1. Replies: 2
    Last Post: 09-10-2018, 09:21 PM
  2. ALARM shuttle drawbar alarm haas
    By timmydabull in forum Haas Mills
    Replies: 28
    Last Post: 02-18-2013, 07:47 PM
  3. Replies: 6
    Last Post: 04-29-2011, 11:20 PM
  4. MV40 major probs
    By BigLozzy in forum Mori Seiki Mills
    Replies: 6
    Last Post: 03-05-2009, 10:20 PM
  5. Alarm 350, not in my alarm list, any ideas?
    By ralph@nes in forum Mazak, Mitsubishi, Mazatrol
    Replies: 4
    Last Post: 09-27-2008, 07:14 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •