586,055 active members*
4,376 visitors online*
IndustryArena Forum > CNC Electronics > Spindles / VFD > 2.2KW Spindle Motor starting problems
Results 1 to 10 of 10
    Feb 2017
    15
    Hello and thanks for any help you can offer in advance.
    I have a 2.2kw spindle motor and Huanyang VFD bought from China as part of building my own cnc machine.
    2 problems:
    1. Sometime but not always the VFD fires up but the moter does not turn? You need to turn the motor manualy then it goes.
    2. Sometimes it runs clock wise and then others anti clock wise but the setting is always set to forward.
    Any help will be greatly appreciated.
    Best, Jono
    Jan 2005
    15362
    Re: 2.2KW Spindle Motor starting problems
    Quote Originally Posted by Jono888 View Post
    2 problems:
    Best, Jono
    You either have it wired incorrectly, ( missing a Phase on the output side of the VFD connection, my be a short in the wiring also ) or the VFD Parameters have been set incorrectly, or both, don't run it until it has been check out
    Mactec54
    Feb 2017
    15
    Thanks. I had the earth connected to the vfd before I posted this and the spindle did not work so I unconnected it and then ran into the problems which I posted (Earth was on pin no1). Bit of back ground data.
    I have checked on a meter and all 3 wires have the correct resistance. No shorts there.
    I reset the spindle to factory settings and then reset the 400hz
    I'm now still at square one with the motor only spinning when I give it a little nudge to spin. It won't start on it's own. (It does appear to sound okay when it runs.)
    Any pointers all welcome
    Jan 2005
    15362
    If you put the earth to Pin # 1 that would of been a major problem, if you still have to spin it, it is either damaged or is still not wired correctly
    The correct wiring for the Spindle Plug to the VFD is Below
    It also sounds you have not set all the correct Parameters, do you have the Parameter I post
    The Ground still has to be connected to Pin 4 and check that the Spindle Pin 4 is also Grounded to the Body of the spindle if not this needs to be corrected
    Mactec54
    Feb 2017
    15
    Many thanks.
    Could have the wiring wrong - lol I will follow your picture
    No I don't have the Parameter I post - what is that.
    I feel there is hope thanks again
    Jan 2005
    15362
    Many thanks.
    They need to be set as I have Posted
    Huanyang Mactec54
    PD000=0 for Parameter unlock ( 1 ) for Parameter Lock
    PD001=0 (1 For Remote Control)
    PD002=0 ( 1 For 0-10v Terminal Control or Remote Trim Pot Control )
    ( J1 Also Needs to be set for Terminal Control )
    PD003=400
    PD004=400
    PD005=400
    PD007=20
    PD008=220 (120 If you have 120v VFD )
    PD009=15
    PD010=8
    PD011=120 ( 100 Minimum Setting with Quality VFD, 120 is Safe)
    PD13= 08 is for Factory reset, Only use this to set VFD to Factory Default Settings
    PD014 Acceleration=12 ( Adjust to suit)
    PD015 Deceleration=12 (Adjust to suit)
    ( PD15 is ignored IF PD26=1 Then the Spindle will Coast to a Stop)
    PD141=220 ( Motor Rated Voltage ) (120 for VFD Rated for 120v )
    PD142= ( Motor Max Amps)
    PD142=( 220vSet for your motor Amp Rating 2.2Kw Spindle 9 amp )
    PD142=( 220VSet for your motor Amp Rating 1.5Kw Spindle 7 amp )
    PD142=( 220v Set for your motor Amps Rating 800w Spindle 4 amps )
    PD142=( 120v Set for your motor Amp Rating 800w Spindle 7 amp )
    PD143=2 ( Motor Number of Poles)
    PD144=3000 (Max Motor RPM) =3,000= (24,000)
    PD70=0 ( This may need to be set to 1 if Control Voltage is 0-5v )
    PD72=400
    PD73=120 ( 100 Minimum Setting )
    Mactec54
    Feb 2017
    15
    You are wonderful!
    The wiring per your diagram was wrong so I have changed it to fit the diagram and now everything appears to run smooth. It starts up by it's self and turns the right way each time.
    Many thanks for the settings. I will go through each one and double check they are correct.
    Really, you have helped me out no end. I thought I had walked into a brick wall with this one and seen one too many you tube videos of the blind leading the blind lol
    Again many thanks! Best Jono
    PS if you have any data on setting up the VFD to Mach3 as this is going to be a close in the future step I would really appreciate that.
    Jan 2005
    15362
    You are wonderful!
    Yes there are many Videos out there, that lead you up the path to disaster, you got lucky, that you did not smoke something
    Make sure your spindle 4th pin is Grounded to the spindle Body most are not, and you have to fix this, something like this attached photo
    You need to make sure your Parameters are set before you run it, you can smoke VFD or Spindle if they are not correct, your spindle can run with incorrect set Parameters
    So Check them before you run it again
    Mactec54
    Nov 2019
    Can you please send the wiring picture? I think this is my problem, but I can't see the photos you attached.
    Thanks!
    Nov 2019
    You are wonderful!
    Can you please send us the wiring diagram? We are having the same exact issue & can't see the one that mactec54 sent you.
    Thanks!
  1. Spindle not starting with TSC on
    By JMFabrications in forum Haas Mills
    Last Post: 04-01-2017, 10:37 PM
  2. KX1 Spindle Motor Speed Problems
    By Steamboat Ed in forum Uncategorised MetalWorking Machines
    Last Post: 11-20-2015, 08:27 PM
  3. spindle starting on its own
    By endgrainguy in forum CNC Machine Related Electronics
    Last Post: 06-26-2014, 02:51 PM
  4. Problems starting up Heidenhain Tnc155
    By Oviksnc in forum CNC Machine Related Electronics
    Last Post: 12-18-2008, 10:54 PM
  5. Spindle Starting Problems
    By dkaustin in forum Tormach Personal CNC Mill
    Last Post: 08-07-2008, 12:09 AM