![Quote](images/misc/quote_icon.png)
Originally Posted by
RCaffin
I can understand the economics of skipping the neutral wire, but its absence is KNOWN to cause a lot of problems. For instance ...
I do not understand what is meant by 'the wild leg' here. If you mean two phases were at 239 V and one phase was at 199 V, I would be having kittens! That is a seriously UNbalanced supply and WILL cause significant problems. For that matter, it means the supply is way overloaded on one phase. NOT GOOD. If it means something else I am just confused.
Roger
If you Google wild leg or high leg Delta it will explain the setup, the neutral is not necessary on the feed to most CNC machines, just the 3 ph supply.
High leg delta is not used very much nowadays.
RCaffin
Yup, fits in.
One thing is very clear to me already: your problems are coming in on the supply, imho.
Cheers
Roger
I agree, this is why I think that monitoring where the trouble ends up, and that is at the 100v 200v control is probably the easiest.
Al.
Albert E.