    Mazatrol fusion PC 640
    Please to help alarm 33 emergency stop when i started to run that machine in the morning.
    I have Checked at main board control unit.
    DC IN LED IS GREEN
    DC OUT LED IS GREEN
    PS EMG LED IS OFF.
    BAT ALM LED IS OFF
    I don't have electrical manual and ladder manual
    Appreciate you.
    Yude
    Oct 2003
    321
    look at all servos, what you can see in the display.
    Best regards
    WWW.servotek-service.com
    Gesendet von meinem PAP5000DUO mit Tapatalk
    Aug 2010
    8
    Alarm led 7 on servo drive and spindle drive.
    thank you and best regards,
    Attachment 219294
    Oct 2003
    321
    OK. E7 is for emergency stop. Look also at MR-J2 for turret oder ATC or table.
    type of the machine?
    Best regards
    Servotek
    Aug 2010
    8
    Hello,
    Mazak Model : QT-200
    Alarm led at MR-J2 are : AL-02-91-N1-01.
    best regards,
    Oct 2003
    321
    This is also emergency stop. May be you get the emergency stop from outside. Have the machine a bar feeder.
    Send a picture from page alarm history ( 3 pages )
    Best regards
    Servotek
    Aug 2010
    8
    Dear Mr.Mazak,
    M/C don't have bar feeder.Please see attachment for alarm history.
    Thanks & best regards,
    Attachment 219444Attachment 219446Click image for larger version.
    Oct 2003
    321
    you find out what happens?
    Feb 2009
    6028
    Says right there. Breaker trip 201. PLC is not up and running. Check circuit breakers first, then start checking power supplies.
    Aug 2010
    8
    Thank you for your reply.
    i checked in the ladder diagram y1output is not actif caused of signal from X241 is not energize.i don't find x241 where come from.
    Best regards.
    Aug 2010
    8
    i checked there are no breaker trip so power supply is ok.
    best regard,
  1. Mazatrol PC Fusion 640 Hang
    By flomatic in forum Mazak, Mitsubishi, Mazatrol
    Last Post: 05-25-2021, 12:31 AM
  2. 4 days on Mazatrol Fusion
    By rmarchjr in forum Mazak, Mitsubishi, Mazatrol
    Last Post: 07-10-2011, 03:15 PM
  3. Mazatrol PC Fusion 640M
    By mfugs in forum Mazak, Mitsubishi, Mazatrol
    Last Post: 02-19-2011, 06:06 AM
  4. MAZATROL FUSION 640 ...not booting...
    By dinudesign in forum Mazak, Mitsubishi, Mazatrol
    Last Post: 11-18-2009, 10:12 PM
  5. mazatrol pc-fusion 640 error....
    By monkei in forum Mazak, Mitsubishi, Mazatrol
    Last Post: 06-03-2006, 12:42 AM