    # 2044 I/O Link Turret Alarm

    My turning Machine is Goodway.
    The alarm is "# 2044 I/O Link Turret Alarm"
    I can't change the tool on the turret.
    Please help me and guide the steps to solve this problem.
    By the way, POWRT MATE CNC MGR have the Warning "416"

    my gmail is [email protected]

  2. #2
    Join Date
    Oct 2005
    Posts
    3

    Re: # 2044 I/O Link Turret Alarm

    Hello!
    I have the same problem. Did you found a solution?

  3. #3
    Join Date
    Dec 2009
    Posts
    977

    Re: # 2044 I/O Link Turret Alarm

    Inverter IPM Alarm has been issued.
    416

    (1) Check whether the cooling fan is not stopped.
    (2) Check whether the motor is used within related current.
    (3) Check whether the temperature in locker is higher. Check the fin or filter
    in locker.
    (4) Check whether the temperature is higher around the servo amplifier
    module.
    (5) Disconnect the power line from the servo amplifier module connector.
    Then, release the emergency stop state.
    - If the IPM alarm continues to be issued, replace the servo amplifier
    module.
    - If no IPM alarm is issued, go to (6).
    (6) Disconnect the power line from the servo amplifier module connector.
    Then, check the insulation between the ground and each of U, V, and W.
    - If the insulation is satisfactory replace the servo amplifier module.
    - If the insulation is not satisfactory, go to (7).
    (7) Disconnect the power line from the servo motor. Then check the
    insulation.
    - If the insulation of servo motor is not satisfactory, replace the servo
    motor
    - If the insulation of power line is not satisfactory, replace the servo
    amplifier module.

  4. #4
    Join Date
    Oct 2005
    Posts
    3
    Quote Originally Posted by zavateandu View Post
    Inverter IPM Alarm has been issued.
    416

    (1) Check whether the cooling fan is not stopped.
    (2) Check whether the motor is used within related current.
    (3) Check whether the temperature in locker is higher. Check the fin or filter
    in locker.
    (4) Check whether the temperature is higher around the servo amplifier
    module.
    (5) Disconnect the power line from the servo amplifier module connector.
    Then, release the emergency stop state.
    - If the IPM alarm continues to be issued, replace the servo amplifier
    module.
    - If no IPM alarm is issued, go to (6).
    (6) Disconnect the power line from the servo amplifier module connector.
    Then, check the insulation between the ground and each of U, V, and W.
    - If the insulation is satisfactory replace the servo amplifier module.
    - If the insulation is not satisfactory, go to (7).
    (7) Disconnect the power line from the servo motor. Then check the
    insulation.
    - If the insulation of servo motor is not satisfactory, replace the servo
    motor
    - If the insulation of power line is not satisfactory, replace the servo
    amplifier module.
    Thank you!
    Actually problem was solved by disconnecting the encoder cable.

Similar Threads

  1. Replies: 26
    Last Post: 03-02-2023, 11:25 AM
  2. GLS-150 Ex 1044 I/O link turret alarm
    By anabolik197801 in forum Fanuc
    Replies: 2
    Last Post: 04-01-2016, 05:53 AM
  3. About # 2044 I/O Link Turret Alarm
    By rubicvn in forum Fanuc
    Replies: 2
    Last Post: 09-05-2015, 10:23 AM
  4. alarm turret 1000 turret conuter error
    By aaagt78 in forum Fanuc
    Replies: 0
    Last Post: 04-08-2015, 04:14 PM
  5. Tool Turret Fault Alarm on TL-1 with no Turret?
    By Edster in forum Haas Lathes
    Replies: 10
    Last Post: 02-08-2010, 03:35 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •