Quote Originally Posted by vbquick1 View Post
I am working with a 110v 1.5kw vfd with a pot control on the front panel. I attempted to configure to the settings in this post and the vfd will not take them. I change a pd setting from 110 to 220 and hit set. I'll check it again and it will still be at 110. I am trying to get full rpm out of my 800w 220v spindle. It currently only reaches 11520.

Sean
I have no information on a 800W Spindle, I thought they were a DC motor, if they are then you can not use this VFD to run it, It has to be AC 3 Phase to be able to use the VFD you have, I see they do have some 800w spindles that are 3 phase, all the setting below will be correct except for the Amp settings, let us know what you are using for that amp setting

If it won't take the settings you have the lock on PD000=0 you will have a (1 ) for this parameter, it needs to be 0

Here are all the correct settings for your Drive

Huanyang Mactec54
PD000=0 for Parameter unlock ( 1 ) for Parameter Lock
PD001=0 (1 For Remote Control)
PD002=0
PD003=400
PD004=400
PD005=400
PD007=20
PD008=220
PD011=120 (Minimum Setting 120)
PD009=15
PD010=8
PD13= 08 is for Factory reset, Only use this to set VFD to Factory Default Settings
PD014 Accel=12 ( Adjust to suit)
PD015 Deccl=12 (Adjust to suit) ( PD15 is ignored IF PD26=1 Then the Spindle will Coast to a Stop)
PD141=220 ( Motor Rated Voltage )
PD142=9 ( Motor Max Amps) (Set for your motor Amp Rating 2.2Kw Spindle 9 amp Max)
(Set for your motor Amp Rating 1.5Kw Spindle 7 amp Max)
PD143=2 ( Motor Number of Poles)
PD144=3000 (Max Motor RPM) =3,000= (24,000)