Can the button FEED HOLD be activeted from parameters or i need to make modification in ladder?
Dear Buterchi.
Usualy the FEED HOLD button activated in ladder and named as *SP( G008.5), the LED is *SPL(F000.4). You can see the status of these signal by selecting PMC-> PMCDNG-> STATUS-> key in G08-> Enter and see on sreen( remember that Fanuc named the address as 7-6-5-4-3-2-1-0, that's mean the righ most work is .0), or you can tracking it by entered it's address in ladder monitor( usualy it's allways used OC contact, what's that meaning of * signal).