    Toroidal transformer build

    I built a PSU with a toroidal transformer, dual input 115v, dual output 50v, wired in series on the input and parallel on the ouput.

    See attachments for what I did, I have an usually high input voltage from the grid it fluctuates but today I was getting 250v in which gave me 78.2v out on my toroidal transformer build.

    I have AM882's and I think I may have already blown one up (At least it doesn't work and I've bought a new one) so do not want to damage them.

    Will I be ok with this voltage, I am in the UK so should be getting ~240v.

  2. #2
    Join Date
    Dec 2013
    Posts
    5722

    Re: Toroidal transformer build

    If your voltage is consistently high, you could take a few turns off of the secondary and reduce the output voltage. Not sure how many you would need to take off, but you can measure the input voltage and the output AC voltage and calculate the Turns Ratio TR = ACVin/ACVout. DCVout = ACVout * 1.414 From this you could figure out how many turns to remove to get you desired max DCV out.
    Jim Dawson
    Sandy, Oregon, USA

  3. #3
    Join Date
    Mar 2003
    Posts
    35538

    Re: Toroidal transformer build

    I've heard that Leadshine's aren't too tolerant of opervoltage, so 78V may be a bit risky.
    Gerry

    UCCNC 2017 Screenset
    http://www.thecncwoodworker.com/2017.html

    Mach3 2010 Screenset
    http://www.thecncwoodworker.com/2010.html

    JointCAM - CNC Dovetails & Box Joints
    http://www.g-forcecnc.com/jointcam.html

    (Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)

  4. #4
    Join Date
    Mar 2007
    Posts
    2083

    Re: Toroidal transformer build

    whats the spec for the transformer

    the 50V output is when the transformer is fully loaded
    off load ( depending on the transformers size ) is likely to be 2 or 3 % higher
    [small 10VA transformers can be 10% higher]

    in my part of the UK , during the day , the main voltage voltage varies between 243 V & 248V

    so I would have to increase the expected 71V DC (50 x 1.4142) by 11% ( 248/230 x 1.03 = 1.11)

    the resulting DC output will be about 79V off load which is at the upper limit for the AM882 drivers

    the added problem is the returned energy
    when a moving part of your machine is rapidly decelerated and drives the motors round , turning them into electrical generators

    this added current will increase the stepper drivers DC supply voltage !
    possibly enough to destroy your stepper drivers

    ( some systems have a returned energy dump to automatically add a high current load to the power supply to limit the maximum voltage due to any returned energy )

    it looks like you need a 45V transformer which will give you about 70V DC


    John

Similar Threads

  1. toroidal transformer sizing
    By paulus.v in forum CNC Machine Related Electronics
    Replies: 0
    Last Post: 10-21-2013, 10:56 AM
  2. toroidal transformer
    By eloid in forum CNC Machine Related Electronics
    Replies: 1
    Last Post: 03-11-2008, 06:21 PM
  3. toroidal transformer
    By cueshark in forum CNC Machine Related Electronics
    Replies: 1
    Last Post: 05-05-2007, 03:31 AM
  4. Help with toroidal transformer
    By CAM_MAN in forum CNC Machine Related Electronics
    Replies: 7
    Last Post: 11-16-2005, 02:35 AM
  5. Help with Toroidal Transformer
    By bill south in forum CNC Machine Related Electronics
    Replies: 6
    Last Post: 08-02-2005, 08:40 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •